Operation Rname, Cname, Tname, name these variables is a power failure to save ? That is, when the system is powered down , (by jili wang)
Operation Rname, Cname, Tname, name these variables is a power failure to save ? That is, when the system is powered down,
the current value of whether it can be saved . Especially Cname and name variable
(no subject) (by Jonathan Westhues)
Look at the "Make Persistent" op, which causes a variable to get automatically saved to EEPROM every time that it changes (and loaded from EEPROM at startup). This will cause that variable to persist across power-on reset.
(no subject) (by Jonathan Westhues)
Are your inputs and outputs active-low? That may happen, for example, if a switch input is wired to ground with a pull-up resistor, or an LED is wired from Vdd to the pin. In that case, turn-on and turn-off will of course be interchanged.
To avoid that, make the electrical input signals active-high, or invert them in software, by marking their contacts and coils as negated.